I'll disagree with Ron on this one.
In the regions in which I've practiced, the usual practice is to turn the hooks outwards. It promotes constuctability. It makes footing dowel cages more stable and it makes it so that the hooks don't interfere with the pouring of concrete into vertical elements.
I feel that the direction of the hook has a huge impact on the fundamental behaviour. Bars hooked outwards are developed but usually not anchored.. Vertical bars in tension are usually in tension due to applied moments. In such cases, the goal of the vertical reinforcing in the joint is to anchor the compression strut emanating from the other side of the member (flexural compression block). As a result hooks in make the most mechanical sense.
In general, good practice is for hooks to always face the compression struts that they are meant to constrain.