One of our 230 kV stations in the farther-flung northern reaches of the province was not provided with any means of remote or transfer circuit tripping from operations of the transformer differential protection; instead, it had a high-speed vacuum ground switch on the transformer side of the high-voltage disconnect switch, wired to close on bank diff. The circuit's reclosure time delay was a few seconds longer than it took for the primary switch to open.
Indeed, back in the day when the highest voltage on our system was 115 kV, auto-grounds were routinely used to trip off banks on differential protection; by convention, these were all wired to the blue phase to provide reasonable assurance that any circuit auto-reclosures had been initiated by a transformer diff trip somewhere out there. One would wait for the "power off" calls to come in to find out which one...
CR