Sdpaddler50
Mechanical
- Aug 30, 2012
- 200
Racks to 15 ft with class 1-3. Sprinkler densities and the usual stuff is generally ok. One, 50 ft long rack section is right up against a glass window on the exterior wall of the building. Dont ask me the rating, i have no idea, but it is tempered glass so it may last a few minutes. The area was probably originally designated for offices, and then storage was likely brought in later. Anyone deal with this situation? Issues? Governing codes; 09' IBC/IFC (actually Cal versions) and NFPA 13, 2010. BTW, i am not going to ask for exposure sprinklers on these glass walls. It would not do any good for the fuel loads involved with the racks. My premise is basically; Storage is adequately protected by the sprinklers, so a fire is controlled in the incipient stage. Plenty of means of egress available to occupants in warehouse. Damage to windows occurr, but nothing major. Overall, fire is controlled and the building lives to ship product another day. Thanks.