Hello there.
I have an issue that has been there for a while, but I dont think I can ignore it any more since some caps from the power factor correction gear blew up a while back. Another problem which can be related to this is the current from the generators jumping radically between 900A and 600A in two seconds.
Setup:
One 625kVA and one 750kVA generator connected to a bus on the LV side of a wye/delta, 0.415kV/11kV 1500kVA transformer. Both generators only operate in parallel mode.
Both generators have their neutrals connected to the busbar neutral, which is in its turn earthed. Also connected on the LV bus are a couple MCC's with a total maximum load of around 1000kVA. I must also mention that some large VSD's are fed from these MCC's.
I have recently measures the I,V and harmonics directly above the feeder isolator that comes from the 1500kVA transformer.Just to be spefific, the measurement was taken before the busbar branches out to the generators and MCC's.
Attached is a graph of my findings.I will attach both a THD and V/I graph for the period of interest.
Take note of Friday 07:27. Before that instance, the generators were connected to the grid, and the neutral current was the same magnitude as the A and C phases. As soon as the GCB tripped, the power went up (more power needed to be supplied by the grid) but the neutral current went right down to zero.
1)If there are harmonics present due to the non-linear load, shouldnt it stay present regardless of the generators coming on and off the grid?
2) Can the harmonics be generated by the generators?
3) Is the generators somehow uncovering the existing harmonics in the system?
I think most of the issues are related to harmonics, but please help me to figure out if there is a way of minimising these effects and if not, what can be done. Filters? Transformers?
Please share some thoughts on my issues and if you need any more info let me know as I might have left out key information which could in fact point to the issue.
I have an issue that has been there for a while, but I dont think I can ignore it any more since some caps from the power factor correction gear blew up a while back. Another problem which can be related to this is the current from the generators jumping radically between 900A and 600A in two seconds.
Setup:
One 625kVA and one 750kVA generator connected to a bus on the LV side of a wye/delta, 0.415kV/11kV 1500kVA transformer. Both generators only operate in parallel mode.
Both generators have their neutrals connected to the busbar neutral, which is in its turn earthed. Also connected on the LV bus are a couple MCC's with a total maximum load of around 1000kVA. I must also mention that some large VSD's are fed from these MCC's.
I have recently measures the I,V and harmonics directly above the feeder isolator that comes from the 1500kVA transformer.Just to be spefific, the measurement was taken before the busbar branches out to the generators and MCC's.
Attached is a graph of my findings.I will attach both a THD and V/I graph for the period of interest.
Take note of Friday 07:27. Before that instance, the generators were connected to the grid, and the neutral current was the same magnitude as the A and C phases. As soon as the GCB tripped, the power went up (more power needed to be supplied by the grid) but the neutral current went right down to zero.
1)If there are harmonics present due to the non-linear load, shouldnt it stay present regardless of the generators coming on and off the grid?
2) Can the harmonics be generated by the generators?
3) Is the generators somehow uncovering the existing harmonics in the system?
I think most of the issues are related to harmonics, but please help me to figure out if there is a way of minimising these effects and if not, what can be done. Filters? Transformers?
Please share some thoughts on my issues and if you need any more info let me know as I might have left out key information which could in fact point to the issue.