I don't think you need this since the generator is designed to withstand the maximum permitted torque. Major functions of a foundation are to:
Support the total weight of the generating set.........
In addition the set must withstand the equal and opposite torque of the driving torque. Add to that the torque developed from the rotor and prime mover inertia when a severe fault causes an abrupt de-celeration. I remember an old motor-generator type welding machine with a problem which some internal connections. When the welder tried to strike an arc, the machine would try to stall the rotor and the whole machine would tip up on one skid. This was scary enough with a shop welder, I wouldn't want to see it happen with a Megawatt class machine.
As well, I seem to remember a thread some time ago concerning inspections for possible foundation damage when a large machine had been subjected to a severe fault.
I agree with electricpete with the following proviso; de-celeration torque is possible.
However if you have been supplied with the torque under short circuit conditions this should be included.
Bill
--------------------