Help in Calculation 1
kingbambina
12
I have a 400V, 10kVA UPS that will be fed from a 480V panel through 15kVA, 480/400V delta/wye transformer. I just want to confirm my calculations. I will take the power from 25A breaker with a 3C 10mm² power cable to the transformer. From the transfomer I will run 3C 10mm² + 4mm² ground to 25A disconnect switch and lastly to the UPS. Is this good?
25A is a little light for feeding a 15kVA transformer at 400V since it should only be loaded to 80%. For wire sizing follow your local electrical codes.
Dear Mr. kingbambina
1. From the voltage (400V) and the wire size (xx mm2), it seems to be in the IEC world,
2. Please tell us to complied with which standard/regulation/Code/location e.g. IEC (International), BS (Great Britten only), NEC (US), CSA (Canada).... etc. Any local regulation/national regulation/Code that is applicable at the location of the installation,
3. I raised this request because the requirements differ.
Che Kuan Yau (Singapore)
In my opinion, you are in USA and have to supply IEC standard equipment -the source it is 480 V as standard in U.S.A. and the UPS supplies 400 V. We don't know the frequency-60 Hz in USA and 50 in Europe. We don't know the length of cables. We don't know what is the actual load on the transformer 480/400- if except the UPS you need 400 for other loads and if the cable run in conduit or other.
I think the cable 10 mm^2 it is a PVC insulated [ 70 oC rated temperature] copper conductors, 4 conductors [3 lives and a neutral].For grounding you have another 10 mm^2 copper -insulated or bared.
The UPS rated current has to be 14.5 A
According to BS7671/2008 Table 4D2A for multicore 70 oC thermoplastic insulated and thermoplastic sheathed non-armoured cables (COPPER CONDUCTORS) one cable in conduit the ampacity [current carrying capacity] will be 39 A.
From table 4D2B the impedance [in mV/A/m] is 3.8 [0.0038 ohm/m] This impedance includes the factor √3 for three-phase system.
If the permissible voltage drop will be 3% [400*3%=12 V] then the maximum length will be 12/0.0038/14.5=217.7 m
Dear Mr kingbambina
@ Mr. 7anoter4
1. Thank you for your learned advice. BS 7671 complied with IEC. Therefore, it is applicable in the IEC world.
..... " .....I think the cable 10 mm^2 it is a PVC insulated [ 70 oC rated temperature] copper conductors, 4 conductors [3 lives and a neutral].For grounding you have another 10 mm^2 copper -insulated or bared....The UPS rated current has to be 145 A...". are in order.
2. Mr.kingbambina FYI: Per BS 7671/IEC [earthing conductor size Sp] = [phase conductor S =< 16mm2]. That is to say that the earthing conductor shall be 10mm2. Your proposal earthing conductor of 4mm2 is NOT acceptable.
Oops, 25A is fine for a 15kVA transformer being fed from 480V.
Considering the Ampacities as given in IEC 60364-5-52, and the derating factors given in this std, you are still good with a 4 sq.mm cable, based on ampacity. Method D - laid in ducts, Method D2 - laid in ground and Method E - laid in tray give ampacities 35A,39A and 42A reply. You may take 6 sq.mm to keep it safe. I do not know the specific laying conditions to eomploy the derating factors.