I have designed, built & installed a home made solar hot water heating system and know roughly the energy gained. I have done some research and come up with a basic calculation for energy transfered in to the hot water storage but would like opinions as to how accurate it is.
I have made my own micro-controller and have many temeperature sensors around the system. I have also measured the flow with an accurate meter. Data I have is:
1. Heat exchanger coil is 22mm copper pipe formed in to 5 coils with a centerline diameter of 0.33m.
2. Heat drop across the heat exchanger coil in degrees C, ie. input and output temperature.
3. Flow rate of 4.0LPM.
I calculated the volume of the heat exchanger coil:
V = (0.011^2 x pi) x (0.33 x pi) x 5 = 1.97 x10-3 m^3
as there are 1000Cu liters per cu meter the volume is
V = 1.97 liters (1.97Kg)
assuming there are no losses/reductions through the copper wall (scale will not form) then the heat lost from the heat exchanger coil:
Q = 4.19 x DT x volume
Q in Mj
4.19 is specific heat capacity of water
DT is differential temp in K or C
volume in Kg.
Considering the flow rate of 4Kg/min
volume = 4
Q = 4.19 x 2 x 4 = 33.52Mj/min
per hour
Q = 33.52 x 60 = 2011.2Mj/hr
Convert to Kw/h multiply by 0.27777
Kw/h = Q x 0.2777 = 2011.2 x 0.2777 = 0.558Kw/h
This figure seems believable but I am not sure if I have made the right assumptions regarding the flow rate and heat exchanger capacity! Knowing the flow rate does the heat exchanger capacity matter?
How much difference would taking the thickness of the copper wall of the heat exchanger in to account affect the outcome?
I have made my own micro-controller and have many temeperature sensors around the system. I have also measured the flow with an accurate meter. Data I have is:
1. Heat exchanger coil is 22mm copper pipe formed in to 5 coils with a centerline diameter of 0.33m.
2. Heat drop across the heat exchanger coil in degrees C, ie. input and output temperature.
3. Flow rate of 4.0LPM.
I calculated the volume of the heat exchanger coil:
V = (0.011^2 x pi) x (0.33 x pi) x 5 = 1.97 x10-3 m^3
as there are 1000Cu liters per cu meter the volume is
V = 1.97 liters (1.97Kg)
assuming there are no losses/reductions through the copper wall (scale will not form) then the heat lost from the heat exchanger coil:
Q = 4.19 x DT x volume
Q in Mj
4.19 is specific heat capacity of water
DT is differential temp in K or C
volume in Kg.
Considering the flow rate of 4Kg/min
volume = 4
Q = 4.19 x 2 x 4 = 33.52Mj/min
per hour
Q = 33.52 x 60 = 2011.2Mj/hr
Convert to Kw/h multiply by 0.27777
Kw/h = Q x 0.2777 = 2011.2 x 0.2777 = 0.558Kw/h
This figure seems believable but I am not sure if I have made the right assumptions regarding the flow rate and heat exchanger capacity! Knowing the flow rate does the heat exchanger capacity matter?
How much difference would taking the thickness of the copper wall of the heat exchanger in to account affect the outcome?