cjhut
Electrical
- Nov 11, 2009
- 43
I have a question concerning harmonics. We have a 240v single phase lighting panel that is feeding some 400w metal halide high bay lighting fixtures. The main CB is 100A and the branch circuits are 20A. When all of the lights are turned on the main breaker is seeing about 50 amps. Each of the branch circuits are only seeing about 10amps. The branch circuit conductors are all on the same conduit for about 10feet before they branch out from a junction box. However, they have been derated appropriatley and are 10guage. From day one when this panel was installed, the circuit breakers seemed to be unusually warm. The conductors are fine, but even the main breaker is warm. An infrared temp gun shows temps of 150 defF on the breakers, in 70 deg ambient temperature. Being that heat seems to be transferring from the brakers themselves, and the currents are by no means excceding any of the ratings, it must be harmonics generated by the all inductive load of the ballasts. This wasn't a cheap panel. I used a Seimens bolt-in type panel. I am wondering what I did wrong, and how do I prevent this in the future. Also, if someone could give me a simplified harmonics explanation, it would be nice.