Grout Filled Bond Beam Strength

Status
Not open for further replies.

jgraham114

Structural
Dec 18, 2012
10
I have a project that is using channel embeds in grout filled bond beam. They are the new Hilti channels so they don't have any real data for them.

Basically, what I'm trying to determine is whether 3000 psi grout filled bond beam is the same strength as 3000 psi normal weight concrete?
 
Replies continue below

Recommended for you

My experience is that 'plain' grout tests at 800-1000 psi, and non-shrink equipment grout tests at 6000 - 9000 psi. Never seen any 3K grout.

ASSuming that you have 3000# compressive strength, you have 3000# compressive strength. Period. Doesn't matter if it is 'grout', 'pump-mix', straight cementious concrete, or epoxy. It's still 3000#.

To keep from having an incipient disaster, you need to take [and crush] grout cubes or regular test cylinders from each batch mixed up. If you calc'd based on 3K, you better not have any 800# grout in the beams.
 