First, I think you have to replace the copper lug with other compatible to steel contact-for instance Burndy or equivalent. Second, if your Electrical Code-as NEC does, for instance-allow to use an insulated grounding conductor replace the actual bare conductor by a pvc insulated one.
As another option you may keep the actual conductor and cover it by a RTV Silicon Rubber layer.
See-for instance:
The colour could be a problem in order to meat the Code requirement.
 
I see either insulated copper wire or braided straps made of tinned copper for similar bonding jumpers.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 