I've never used any mandated spacing of construction joints in concrete grade beams. The spacing of CJ's are left up to the contractor which depends upon crew size, availability of concrete, etc.
In the past, I have specified a limit of 400 cy of concrete in one day's placement - but haven't done that for a while as I think it invades the means and methods of the contractor.
In terms of controlling cracks, etc., I wouldn't think it necessary to use CJ's at all unless the grade beam is some kind of wall system where large areas of concrete were exposed to view. In that case, I'd probably specify vertical formed goove joints near midspan.