I'm a process engineer working on a site with glycol dehydration.
The reboiler in our glycol regeneration unit is supposed to operate at 193degC, but we can't seem to raise the temperature above 185 degC or so.
The glycol is heated in a kettle by condensing steam within tubes. Steam supply is saturated at 16.1 barg (204 degC).
There is no control on the steam flow, rather elevation of the reboiler above the steam supply drum and the steam and condensate lines have been sized to allow sufficient flow for the duty required.The condensate just flows under gravity back to the steam drum.
We have considered fouling of tubes, air in lines and other engineers have checked the elevation of the vessels and insulation.
Can anyone suggest what may be happening here? I guess if the lines are undersized there is a problem. Would there also be a problem with oversized lines?
Any help would be much appreciated.
The reboiler in our glycol regeneration unit is supposed to operate at 193degC, but we can't seem to raise the temperature above 185 degC or so.
The glycol is heated in a kettle by condensing steam within tubes. Steam supply is saturated at 16.1 barg (204 degC).
There is no control on the steam flow, rather elevation of the reboiler above the steam supply drum and the steam and condensate lines have been sized to allow sufficient flow for the duty required.The condensate just flows under gravity back to the steam drum.
We have considered fouling of tubes, air in lines and other engineers have checked the elevation of the vessels and insulation.
Can anyone suggest what may be happening here? I guess if the lines are undersized there is a problem. Would there also be a problem with oversized lines?
Any help would be much appreciated.