et1ying
Industrial
- Jul 2, 2003
- 3
Hello everyone,
We have 2 GE combustions turbines supplying a 300MW Toshiba steam turbine (3 pressures, HP:1200-2400, Reheat: 185-380, LP: 40-60)through 2 HRSG's. During normal operations, our gland sealing steam comes from our Cold Reheat maintaining 4 psig at about 700 degrees Farenheit. When we perform overnight shutdowns, some of our operators run our auxillary boiler to supply gland sealing steam, instead of using the residual heat of the HRSG's to supply the steam (the aux boiler does not swing gland seal pressure during the shutdown period and the HRSG purge period). When our aux boiler supplies steam to the seals, the best steam temperature we get (using an electric superheater) is roughly 250 to 300 degress Farenheit. There is much debate between a few individuals, over the possible damage being done to these seals when cooled from roughly 700 down to an initial 250 degrees and then allowed to build to 300 (due to lag in the superheater response and the heating of the piping between the aux boiler and the gland seal system). Could I get some of your insights and guidance?
Thanks you and have a good day,
Dan
We have 2 GE combustions turbines supplying a 300MW Toshiba steam turbine (3 pressures, HP:1200-2400, Reheat: 185-380, LP: 40-60)through 2 HRSG's. During normal operations, our gland sealing steam comes from our Cold Reheat maintaining 4 psig at about 700 degrees Farenheit. When we perform overnight shutdowns, some of our operators run our auxillary boiler to supply gland sealing steam, instead of using the residual heat of the HRSG's to supply the steam (the aux boiler does not swing gland seal pressure during the shutdown period and the HRSG purge period). When our aux boiler supplies steam to the seals, the best steam temperature we get (using an electric superheater) is roughly 250 to 300 degress Farenheit. There is much debate between a few individuals, over the possible damage being done to these seals when cooled from roughly 700 down to an initial 250 degrees and then allowed to build to 300 (due to lag in the superheater response and the heating of the piping between the aux boiler and the gland seal system). Could I get some of your insights and guidance?
Thanks you and have a good day,
Dan