We have a 500kW genset connected to a 0.415kV/11kV wye/delta transformer.
We operate in parallel with the grid, and at this stage due to the switchgear setup and lack of transfer switches we never operate in island mode.
We have a Deif GPU 3 unit overlooking the protection of the genset. Protection such as under/over frequency and voltage, as well as ROCOF and vector shift is incorporated. We are at the stage of commissioning a second genset connected in parallel with the first one.
The utility is now saying that they want to install an earth fault transformer on the 11kV side for protection.
They are concerned that if there is a fault on the MV side (one of the phases falls to earch) our protection will not be able to pick the fault up, and as a result our gensets will keep energising the potential dangerous earth fault.
Paralleling to the grid is still a fairly new thing around here and it seems like the utility inst sure what sort of protection is needed.Can anyone please shine light on how they go about this issue in other places around the world?
My argument and please correct me if I am wrong, is that if there is such a fault, the utility will trip, causing a vector shift which will in fact be picked up by our relay. Like a loss of mains protection.
If there are any IEC standards or relative literature relating to this issue, please point me in the direction.
Thanks for everyone's input, I learn something new from this website every time I log in.
We have a 500kW genset connected to a 0.415kV/11kV wye/delta transformer.
We operate in parallel with the grid, and at this stage due to the switchgear setup and lack of transfer switches we never operate in island mode.
We have a Deif GPU 3 unit overlooking the protection of the genset. Protection such as under/over frequency and voltage, as well as ROCOF and vector shift is incorporated. We are at the stage of commissioning a second genset connected in parallel with the first one.
The utility is now saying that they want to install an earth fault transformer on the 11kV side for protection.
They are concerned that if there is a fault on the MV side (one of the phases falls to earch) our protection will not be able to pick the fault up, and as a result our gensets will keep energising the potential dangerous earth fault.
Paralleling to the grid is still a fairly new thing around here and it seems like the utility inst sure what sort of protection is needed.Can anyone please shine light on how they go about this issue in other places around the world?
My argument and please correct me if I am wrong, is that if there is such a fault, the utility will trip, causing a vector shift which will in fact be picked up by our relay. Like a loss of mains protection.
If there are any IEC standards or relative literature relating to this issue, please point me in the direction.
Thanks for everyone's input, I learn something new from this website every time I log in.