I have a horizontal hydro unit, 3MVA, and when the excitation is applied to it, a screeching noise starts that is very loud and annoying. Does anybody know the reason for this? I have heard that it has something to do with the way the rotor was made?
 
Replies continue below

Recommended for you

High electromagnetic noise can occur for a variety of reasons... can be inherent in the machine design based on winding configration including number of poles and rotor and stator slots. Can also be increased by eccentricity, overvoltage, and mechanical resonances.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
As pete says, electromagnetic noises are part of the machines. Did this problem pop up suddenly ? Is this a new unit or was recently repaired/refurbished/rewound ?

Muthu
 
This unit has always done this since it was installed in 1985. That is why I was thinking it had to do with the way that the rotor was constructed.
 
construction and installation, do matters with your prob. Try measure step increase of excitation current..note the noise comes out, if it does when excited at a certain level..it may cause probably core.