Be careful, the curves for the CDG do not follow a formula.
The formulas in the PRAG that you mention are for electronic/numerical relays.
If you look at the curve for the CDG14, at 5 times the current setting the relay operates in 2.05 seconds.
If you put the same value into the EI formula, the operating time is 3.33 seconds
If you don't have a copy of the PRAG, contact ALSTOM for a copy of the CDG14 publication.