NAZ55
Electrical
- Oct 24, 2007
- 211
I have a fuse and conductor sizing problem I need help with:
Problem:
MOTOR
Quantity: 32 motors
motor size: 1/3 hp
FLA : 3.6 A @230V
LRC : 14 A
connected phase to phase
SERVICE
240V THREE PHASE SERVICE.
I am trying to determine what size conductor and fuses to use for circuit protection.
My worst case scenario per phase-phase is 6 motors running while six are starting.
SOLUTION:
From FLA
11 x 3.6 + 1.25 x 3.6 = 44.1A = phase current
line current = 44.1A x SQRT(3) = 77A
I therefore can use # 6 wire and 100A NON fuse
but with 6 motors starting at the same time and six running I have
6 x 14 + 6 x 3.6 = 105.6 A = phase current
line current = 105.6A x sqrt(3) = 183A
which is more than what #6 wire and 100A NON fuse could withstand.
Any suggestions?