I have a question about wall arching that's always kind of bugged me.
When you have a wall with no opening there is no arching, each foot of wall carries its own weight for the full height. Simple and it makes sense.
Every lintel example I've ever seen involves arching of the wall (provided there is enough wall left on both sides to resist the thrust), which dramatically reduces the loads for a tall wall.
To look at an extreme example, if a lintel were placed with infinite bending stiffness then it makes sense that no arching would take place.
It seems like the stiffness of the lintel is what does, or does not, allow the arching action to take place. I've never seen any literature on this, though. For almost all CMU or brick lintels, I use the L/600 deflection criteria per ACI 530. This is pretty stiff. Granted, it's not as stiff as the wall that was removed, but it's still pretty stiff. Is it so stiff that the classical arching (where you're designing for the triangular load that starts at 0 plf at the ends) will not take place?
I guess I'm trying to get a sense of how soft a lintel needs to be or how much deflection needs to occur to allow the arching to really start kicking in.
When you have a wall with no opening there is no arching, each foot of wall carries its own weight for the full height. Simple and it makes sense.
Every lintel example I've ever seen involves arching of the wall (provided there is enough wall left on both sides to resist the thrust), which dramatically reduces the loads for a tall wall.
To look at an extreme example, if a lintel were placed with infinite bending stiffness then it makes sense that no arching would take place.
It seems like the stiffness of the lintel is what does, or does not, allow the arching action to take place. I've never seen any literature on this, though. For almost all CMU or brick lintels, I use the L/600 deflection criteria per ACI 530. This is pretty stiff. Granted, it's not as stiff as the wall that was removed, but it's still pretty stiff. Is it so stiff that the classical arching (where you're designing for the triangular load that starts at 0 plf at the ends) will not take place?
I guess I'm trying to get a sense of how soft a lintel needs to be or how much deflection needs to occur to allow the arching to really start kicking in.