Hi all,
Could someone enlighten me on how fuel regulation in generators is achieved? I am aware that this is one of the functions of the governor module but some detail on how it is achieved will be helpful.
Pointers to relevant literature on the web will also be apprecialted.
 
Replies continue below

Recommended for you

Fuel regulation is normally achieved by a control valve acting on the fuel flow in to the engine.

The control valve is normally the output element of a closed-loop control system designed to maintain some parameter at a pre-determined value. That value could be one of the following:

Generator speed held constant under changing load

Generator output held constant under changing frequency (when attached to a larger system)

Generator speed controlled to follow some defined acceleration curve (typically for turbines)

The closed-loop control system will require some sort of sensor to measure whatever the controlled variable is(speed, power, etc) to provide feedback.



-----------------------------------

Start each new day with a smile.

Get it over with.

 
Suggestion: Inquire at Woodwards Governor Co. The fuel control will vary according to the prime mover type.
 
Many newer diesel engines use electronic unit injectors which are timed by a computer.
 