FRANGIBLE ROOF AND COOLING RING 2

Status
Not open for further replies.

judge503

Mechanical
Joined
Jun 21, 2012
Messages
5
I am using a frangible roof for emergency vent and their is a water cooling ring for the roof.
In the case of exposure , the failure will in the roof to shell joint .
how can this failure happens with the existance of the cooling water system which will prevent the roof due to connection with the riser and on roof plates

please advise

thanks in advance
 
Short Answer: It won't work.

Long Answer: It has been proven by MANY tank explosions that it is hard to get the roof-seam to fail. Flat-bottom tanks 'want' to burst at the floor-to-shell joint. And it is essentially impossible to have a frangible roof on a 10-metre/35-ft tank or smaller.

If your tank is 20m / 70-ft or larger, a carefully designed and built frangible roof is possible. The roof-to-compression ring weld must be kept small and 'cold'. A nice 'hot' bead that penetrates both pieces is the last thing you need.

Any restraints or roof reinforcement, like your cooling ring, or a roof platform, or numerous piping attached to roof-mounted nozzles will help hold the roof on, and try to put the failure into the floor-to-shell joint. I would add anchor bolts with 'chairs' to help keep the shell attached to the floor.

With anchors & chairs, and a tiny, 'cold' roof weld, and the cooling ring supported by the shell and unconnected to the roof, a frangible roof may be possible.
 