aayvat
Structural
- Oct 10, 2008
- 11
I'm designing a connection between two light guage steel framing members. The connection will need to withstand a load of 3100lb. I'm looking to use teks fasteners if possible. Otherwise 1/4-20 hex bolts. Need to determine number required and configuration. My question is: when designing for such a connection, must allowable screw loads be met or is it ok to move towards the ultimate screw loads. Big difference between the two. Two 12-14 teks would be enough using ultimate loads whereas I would need atleast 5 considering allowable loads.