jlr899
Industrial
- Nov 14, 2012
- 4
Replacing old Bailey control valve positioners with Foxboro-Eckardt SRD991 intelligent positioners on our waste heat boilers. Worked fantastic until the warmer ambient temps reach into the 90'S at which time they started to overheat and fail until they cool down. Foxboro stated temp rating at 80c (175f). Has anybody else out there had the same problem, and how did you correct it. As of right now we've tubed plant air into the housing to keep them operational, don't want to continue this due to the least bit of moisture will fry the electronics.
Thanks
Thanks