Both austim and haynewp bring up good points. Don't assume they are right, perhaps they just haven't been caught!
For "pre-engineered metal buildings" (I just love this term! It implies all our other buildings are post-engineered!), the soil bearing capacity is usually not a big deal since column loads are usually pretty small. The critical loading is resistance to uplift (and overturning). As haynewp noted, a safety factor of 1.5 is required (under most codes). This factor may be couched in other language such as " the overturning moment shall not be greater than 67 percent of the dead load resisting moment" or other similar language.
Anyway, the way to cover this is to tie as much of the foundation and slab together as you can. A "turn-down" slab (thickened edge) is often used with a 10-foot perimeter of the slab tied into the edge with reinforcing to create a greater dead load uplift resistance. Your competitors might be thickening only the area under the columns and not the entire perimeter. This requires a thicker section and more reinforcement than a perimeter thickened edge approach. Don't forget joint the slab at the end of the reinforcing or you'll get odd crack patterns.
good luck