dakota99
Structural
- Feb 23, 2005
- 21
I have a project that has a 20 foot tall cast in place concrete foundation wall That will be back filled full height with sand. The wall is 14" thick, I am using 30 pcf for my active pressure on the wall. I want to design the wall as pin-pin. the top will be pinned by the main floor diaphragm. How do I achieve a pinned condition at the base? I have a 4000 lb/ft horizontal reaction at the top of footing that I dont know how resolve. Can I use the basment slab as 4"thick x 12" wide column to support the reaction? The slab is 8" above the top of footing so I am ignoring passive pressure. This seems like a very simple issue I think I am just looking at it the wrong way. Please help