Hokie93
Structural
- Sep 9, 2007
- 375
For those who regularly use ASCE 7 in their practice, do you typically take advantage of the 25% reduction in foundation overturning permitted by ASCE 7-10 section 12.13.4? The same provision was included in earlier editions of ASCE 7 as well. My suspicion is that this provision is not widely employed in practice. As I read it, the provision applies strictly to overturning (not sliding) and only applies to foundation members. Of course, you have to meet the limitations set forth in ASCE 7 as well (use of the Equivalent Lateral Force procedure and the structure in question cannot be an inverted pendulum or cantilevered column structure). Since the vertical distribution of seismic forces in the Equivalent Lateral Force procedure is based on the first mode of vibration and that distribution overestimates the overturning force, it makes sense that a reduction in overturning is permitted.