I have a combined footing under uplift (2 columns) reinforced for the positive and negative regions for flexural strength or by the ACI minimum reinforcing requirement.
But can the reinforcing be discontinued where the plain concrete section (designed by ACI 318-05 Chapter 22) is adequate to resist the bending in the top or bottom face of the footing? Or is the intent of 22.2.2 to only be applied to footings that do NOT have uplift? I don't think it matters if it is a combined footing or a single column footing under uplift, my question is can the plain concrete section be used by Chapter 22 to resist the footing's own self weight under uplift if the plain section works by analysis (per 10.5.1)?
22.2.2 — Use of structural plain concrete shall be limited
to (a), (b), or (c):
(a) Members that are continuously supported by soil
or supported by other structural members capable of
providing continuous vertical support;
10.5 — Minimum reinforcement of flexural
members
10.5.1 — At every section of a flexural member where
tensile reinforcement is required by analysis
But can the reinforcing be discontinued where the plain concrete section (designed by ACI 318-05 Chapter 22) is adequate to resist the bending in the top or bottom face of the footing? Or is the intent of 22.2.2 to only be applied to footings that do NOT have uplift? I don't think it matters if it is a combined footing or a single column footing under uplift, my question is can the plain concrete section be used by Chapter 22 to resist the footing's own self weight under uplift if the plain section works by analysis (per 10.5.1)?
22.2.2 — Use of structural plain concrete shall be limited
to (a), (b), or (c):
(a) Members that are continuously supported by soil
or supported by other structural members capable of
providing continuous vertical support;
10.5 — Minimum reinforcement of flexural
members
10.5.1 — At every section of a flexural member where
tensile reinforcement is required by analysis