I get a call today from a contractor on a job we are doing. They began pouring the footing for an 18' retaining wall earlier in the day (90F and sunny). The ready-mix trucks stop coming at about 2pm after getting only 10" down of the 20" thick footing. They finally get a hold of me at home around 4:30pm. At this point the concrete has hardened sufficiently that there will be a horizontal joint at mid-depth when the fresh concrete arrives (the site super was standing on it).
My initial concrens:
1. Will the wall dowels (#9@10) be able to develop fully?
2. Will the top bars in the footing be affected? My "d" went from about 17.5" to about 7.5". Or did it? Will the horizontal shear between planes be adequate to "activate" the bottom half.
3. Generally speaking, should the engineer make a decision on the fly, over the phone, about whether to continue the pour? Or is this purely the contractor's responsibility? If I give him an opinion that is wrong (either keeping it or scrapping it), will I be liable?
In the end, the super decided to cancel his order and start cutting out the concrete before it completely hardened.
Was that the right decision? Opinions, please.
My initial concrens:
1. Will the wall dowels (#9@10) be able to develop fully?
2. Will the top bars in the footing be affected? My "d" went from about 17.5" to about 7.5". Or did it? Will the horizontal shear between planes be adequate to "activate" the bottom half.
3. Generally speaking, should the engineer make a decision on the fly, over the phone, about whether to continue the pour? Or is this purely the contractor's responsibility? If I give him an opinion that is wrong (either keeping it or scrapping it), will I be liable?
In the end, the super decided to cancel his order and start cutting out the concrete before it completely hardened.
Was that the right decision? Opinions, please.