I have a few NEC code questions that I have not been able to have answered to my satisfaction yet, and I am hoping some of you code experts can help me out.
Background:
My company routinely uses #4/0 AWG single-conductor type-W cables and smaller (#6, #4, #2 AWG) multi-conductor type-SOW cables for our portable, temporary power distribution setups. This may include temporary generator(s) powering our own portable distribution systems which in turn power our portable utilization equipment such as air conditioners, air compressors, heaters, cooling towers, etc. Many times we provide power to our customer’s distribution systems in the event of an outage (such as after hurricanes, or in the event of a main transformer failure at a plant), and many times we tie in our portable generators directly to the electric utility to in the event of heavy power demand, or in the event that utility peaking generators fail. All of the installations are performed by qualified personnel.
Questions:
In the above cases, does the NEC permit the use of flexible cables (addressed in article 400) without the use of attachment plugs? For example: Using multiple runs of type-W cable to tie a portable, temporary 1000kW generator to a MCC main breaker at a refinery… with the type-W cable being terminated on 75 degree C lugs on both ends
If yes to question #1, would we still need to apply the requirements of 110.14(c), and hence the ampacity of the circuit must not exceed the rating of the 75 degree C lug based on table 310.16 (of the 2008 NEC), even though the rating of the flexible cord may be much higher? For example: Using a type-W #4/0AWG cable with a 75 degree C lug on both ends and assuming no correction factors for ambient temperature and # of current-carrying conductors in a raceway… the cable ampacity would be 405A, but the termination ampacity would be 230A, so the ampacity of the circuit would be limited to 230A?
I would be extremely happy if you could answer these questions or even point me in the right direction.
Background:
My company routinely uses #4/0 AWG single-conductor type-W cables and smaller (#6, #4, #2 AWG) multi-conductor type-SOW cables for our portable, temporary power distribution setups. This may include temporary generator(s) powering our own portable distribution systems which in turn power our portable utilization equipment such as air conditioners, air compressors, heaters, cooling towers, etc. Many times we provide power to our customer’s distribution systems in the event of an outage (such as after hurricanes, or in the event of a main transformer failure at a plant), and many times we tie in our portable generators directly to the electric utility to in the event of heavy power demand, or in the event that utility peaking generators fail. All of the installations are performed by qualified personnel.
Questions:
In the above cases, does the NEC permit the use of flexible cables (addressed in article 400) without the use of attachment plugs? For example: Using multiple runs of type-W cable to tie a portable, temporary 1000kW generator to a MCC main breaker at a refinery… with the type-W cable being terminated on 75 degree C lugs on both ends
If yes to question #1, would we still need to apply the requirements of 110.14(c), and hence the ampacity of the circuit must not exceed the rating of the 75 degree C lug based on table 310.16 (of the 2008 NEC), even though the rating of the flexible cord may be much higher? For example: Using a type-W #4/0AWG cable with a 75 degree C lug on both ends and assuming no correction factors for ambient temperature and # of current-carrying conductors in a raceway… the cable ampacity would be 405A, but the termination ampacity would be 230A, so the ampacity of the circuit would be limited to 230A?
I would be extremely happy if you could answer these questions or even point me in the right direction.