Hi All,
Please can you comment on the following design solution-
A small village serviced by an exisiting 225mm sewer which drains to a wet well of the inlet of the treatment works. The final 600m section of the main is laid very flat~ 1 in 450 slope. Multiple incident of sewage flooding occured in some private properties due to backing up of sewage. The properties are located 600m upstream of the well. These properties drains to the flat section of the sewer.
Based on spreadsheet calculations and surveys (CCTV, Manhole, Flow monitor), it was confirmed that the existing 225mm mm sewer at the downstream section of flooding properties was undersized resulting in surcharging during storm condition. As a result the sewage backs up from the main sewer into the existing 150mm lateral sewer serving the properties and causing flooding. It was concluded that the main sewer was laid at a slack gradient ~1 in 450; as a result the sewer was susceptible to frequent deposition of debris and grease in dry condition which exacerbated the flooding situation. The existing sewer was laid relatively flat and hence did not comply with engineering standards requirements of 0.75m/s self cleaning velocity.
Due to the hydraulic incapacity problems of the existing system and because of operational problems due blockages in the existing sewers, it was recommended re-grading 600 m length of the main sewer and upsizing from 225mm to 300mm up to the wet well.
The sewer at the wet well was lower 1.72 meters, provided just 0.5m above the pump start level. There is a overflow in the wet well at a high level. In its original condition the exisiting sewer from the village is slightly higher than the strom overflow. WIth the change in the design the new sewer is about 1.75m below the overflwo pipe.
My concern is why the exisiting sewer was laid at such a flat gradient-I can not say that they were lazy! must be reasons behind this.
By regrading the sewer and upsizing the sewer, we are inviting more flow and at a faster rate. During storm conditions when the inflow is greater than the pumped flow, there will be more spill from the overflow unless adequate storage has been provided in the 300mm sewer.
Members, please advice in anyway can be justify the above design. Any thoughts about the above design.
Also, can anyone advice any spreadsheet to calculate storage volume of sewer considering the gradient of the sewer.
Regard
Please can you comment on the following design solution-
A small village serviced by an exisiting 225mm sewer which drains to a wet well of the inlet of the treatment works. The final 600m section of the main is laid very flat~ 1 in 450 slope. Multiple incident of sewage flooding occured in some private properties due to backing up of sewage. The properties are located 600m upstream of the well. These properties drains to the flat section of the sewer.
Based on spreadsheet calculations and surveys (CCTV, Manhole, Flow monitor), it was confirmed that the existing 225mm mm sewer at the downstream section of flooding properties was undersized resulting in surcharging during storm condition. As a result the sewage backs up from the main sewer into the existing 150mm lateral sewer serving the properties and causing flooding. It was concluded that the main sewer was laid at a slack gradient ~1 in 450; as a result the sewer was susceptible to frequent deposition of debris and grease in dry condition which exacerbated the flooding situation. The existing sewer was laid relatively flat and hence did not comply with engineering standards requirements of 0.75m/s self cleaning velocity.
Due to the hydraulic incapacity problems of the existing system and because of operational problems due blockages in the existing sewers, it was recommended re-grading 600 m length of the main sewer and upsizing from 225mm to 300mm up to the wet well.
The sewer at the wet well was lower 1.72 meters, provided just 0.5m above the pump start level. There is a overflow in the wet well at a high level. In its original condition the exisiting sewer from the village is slightly higher than the strom overflow. WIth the change in the design the new sewer is about 1.75m below the overflwo pipe.
My concern is why the exisiting sewer was laid at such a flat gradient-I can not say that they were lazy! must be reasons behind this.
By regrading the sewer and upsizing the sewer, we are inviting more flow and at a faster rate. During storm conditions when the inflow is greater than the pumped flow, there will be more spill from the overflow unless adequate storage has been provided in the 300mm sewer.
Members, please advice in anyway can be justify the above design. Any thoughts about the above design.
Also, can anyone advice any spreadsheet to calculate storage volume of sewer considering the gradient of the sewer.