Fixed Ladder - Stringer Extension Design (Walk-through)

Status
Not open for further replies.

FHErfurt98

Civil/Environmental
Aug 17, 2011
2
I am looking for design requirements for fixed, wall-mounted ladders, specifically the stringer extension that forms the walk-through at the top of the ladder.
OSHA and ANSI provide design requirements but do not specifically call out lateral loading at the top of the stringer end/walk-through. One could apply the IBC point loading for guard railing of 250 pounds. However, this loading would render any flat bar stringer extension unsuitable.
Any comments?
 
Replies continue below

Recommended for you

I have seen ladders with the step-through portion made from angle specifically for this reason. (I would take the design load as what could reasonably be applied by a climber of the rated capacity rather than the guardrail load).

More often, it is possible to either support those bars by tying them into the platform guardrail or by a ladder cage.
 
For practical reasons, you MUST attach the verticals (the bars or supports your hands are "following/sliding upwards as you climb the ladder) smoothly up to the hand rails of the higher stage. At a power plant two weeks ago, a person (me!) climbing the ladder up to the deck entrance could slide their hands up to a gap so that the person (me!) could fall backwards away from the deck.

You're looking for a blame-free design-by-rulebook or design-by-code answer: The right answer is the "how much weight (waht force) is going to be passed through that memeber when a design-sized person gets in that position. So provide a sketch of the problem. Even a 240 lb load can be resisted in tension by a 1/2 x 1/4 bar adequately welded on both ends, even when that 230 lbs is multiplied by a reasonable safety factor, so I do not understand your concern.
 
JStephen and racookpe1978, Thank you for your replies. I will make reasonable loading assumptions for ultimate and deflection design of the stringer.
 