Fire Tank Vent Size

Status
Not open for further replies.

Jeremiah187

Mechanical
Mar 14, 2008
22
Gents,

NFPA 22 says fire water tank vent needs to be minimum of 2".

Somewhere (long ago) i've heard that the tank vent needs to be at least 1 pipe size larger then suction line to fire pump.

Does anyone have any additional information? Or heard of the same requirement.

This job in particular is northern canada.


 
Replies continue below

Recommended for you

4.14.2 A vent pipe shall have a cross-sectional area equal to a minimum of one-half the area of the discharge pipe(s) or fill pipe, whichever is the larger.?????
 
Vacuum is a killer of tanks, tread carefully!

I first determine the MAV (maximum allowable vacuum), then I size a vent to admit air at the rate liquid can leave. Based on atmospheric pressure to the MAV pressure. I use the pumpout on the performance curves at the installed bhp -and- drain valves open. Many will think this is too conserative, but the cost of gooseneck vent is pennies. A collapsed tank is hundreds of thousands.

 
Main Office is Yellowknife, but work includes everywhere from Alert to Iqualuit to Edmonton, Inuvik to Whitehorse....
 
I just may be your next door neighbour!
Drive down into Kam Lake,right on Deh Cho Blvd, and first left is us. Small world.

Regards
Dave

 