Looks like the wording LCREP posted above may have been first in the 07
are they designing the sprinkler system to the 96 nfpa 13 or a newer version??? hopefully a newer version
from 96:::
Chapter 4 Installation Requirements
4-1" Basic Requirements.
4-1.1" The requirements for spacing, location, and position
of sprinklers are based, on the follow!ng.principles:
(a) Sprinklers installed throughout the premises,
(b) Sprinklers located so as not to exceed maximum protection
area per sprinkler,
(c) Sprinklers positioned and located so as to provide satisfactory
performance, with respect to activotion time and
distribution.
Exception No. 1: For locations permitting omission of sprinklers,
see 4-13.1, 4-13.2, and 4-13.8. ~.
Exception No. 2: When sprinklers are specifically tested and test
results demonstrate that deviations from clearance requirements to
structural members do not impair the ability of the sprinkler to control
or suppress a fire, their positioning and locating in accordance
with the test results shall be permitted.
Exception No. 3: Clearance between sprinklers and ceilings exceeding
the maximum specified in 4-6.4.1, 4-7,.4.1, 4-8.4.1, 4-9.4.1,
4-10.4.1, and 4-11.4.1 shall be permitted provided that tests or calculations
demonstrate comparable, sensitivity and performance of the
sprinklers to those installed in conformance with these sections.