Fire pump room requirements 4

Status
Not open for further replies.

chaz12

Mechanical
Joined
Jan 8, 2007
Messages
12
Location
US
Does NFPA 20 require that the pump room be dedicated exclusively to the fire pump equipment? Due to space limitations, we wanted to have a pump room that would contain the hot water and chilled water pumps along with the fire pump. The room is 2 hour rated and will be sprinkled.

Thanks

Chaz
 
where are you sticking this??? high rise, warehouse, one story office building????????
 
NFPA 20, 2007 A5.12.1.1.1 As long as the equipment does not pose a fire hazard, i.e. a boiler, it is OK.
 