Fire-proofing conduit 1

Status
Not open for further replies.

wthall

Electrical
Sep 18, 2002
10
The conduit that supplies my client's fire pump controller with power runs through a room not protected by sprinklers. Is there a product that I can apply (foam, blanket, etc.) to this conduit to make it fire resistant, even fire proof. Re-routing the conduit is not an option.

Thanks...
 
Replies continue below

Recommended for you

Hi WTHall!

I went thru this same situation about 10 years ago. Although the insurance inspectors were willing to let me get by with fireproofing and sheetrock (making the equivalent of a 2-hour enclosure around the conduit), the fellows from construction code enforcement were only willing to accept 4-hour construction as "equivalent protection" (i.e., still didn't meet code). We had to put 4" of concrete around it.

Good luck with your situation!

Old Dave
 
Thanks for the response.

I forgot to mention that this conduit is running through the ceiling joists, about 10' above grade. Concrete doesn't seem like an option.
 
Concrete and MI cable are the only two solutions I'm aware of. The MI cable does sound cheaper, but I wouldn't overlook the concrete option until you get pricing.
 
I have previously bought cable tray protection from a company in Houston ( that is capable of withstanding severe fire (including hydrocarbon fires). You will need to watch out as wrapping power cables in any system may require uo to de-rate the cable to prevent it overheating.
 