in NFPA 13R,there is a good detail for multi dwelling up to 4 story.
but what about more than that,say 10 or 20 stories? I have a building, I want to design fire fighting system for 8 floors apartment depending on NFPA13 & 14.what should I do?
 
apply nfpa 13

oh as above seek professional help
 
at some point you are going to be a high rise
 
You should start by finding the manufacturers data sheets of the sprinklers you propose to use.

You should follow all the conditions of the UL listing regarding flow rates spacing, installation and anything else which is given as a condition of listing.

Also can you tell us about yourself and your project & which country you are in.
 