Robert216
Structural
- Apr 11, 2007
- 35
I know the ACI 318 states that concrete shall have a minimum f'c of 2500 psi. I have a situation where 28 day, 56 day, and even some cored breaks have come in lower (around 2000 psi). Keep in mind that all concrete is for shallow foundations, no vertical elements. I have checked shear and moment capacities in the footings and everything works ok, even when I set f'c=1500 psi. I also checked epoxied anchorage and "backed into" published values from Hilti for masonry (min. f'c=1500 psi). Is there any other potential problem that I should be aware of? Thanks in advance for any help. Rob