Currently overhauling a 110 MW generator at client’s site. Major observations as under:
1. Rotor has an interturn short – impedance is reduced by 17 % compared to the factory values. Surge waveform shows separation when tested from either end (+ve & -ve). Cleaning did not help.
2. Generator shaft is magnetized, as are the centering rings of the endbells.
3. Bearing insulation resistance was 2 megaohms.
4. Exciter end bearing shows electrical pit marks, but not in the load zone.
5. About 20 grub screws used to lock the rotor wedges were missing. Located 14 so far, some stuck in the stator ventilating ducts. Many rotor wedges were thus loose.
6. Boroscope inspection under the retaining rings did not reveal any abnormality.
7. One rotor coil has shifted axially leading to partial blockage of some of the ventilating holes.
This is a 7 year old gas turbine generator which is started every day morning, run at full load & shut down at night (first time I’ve seen this).
Answers/opinion sought:
1. How often do you run generators with rotor interturn shorts? I have seen two earlier, but with minor impedance reduction (surge test would show separation of the waveforms).
2. At what percentage of impedance reduction would say that a repair is a must?
3. Is there any way in which the shaft magnetization & interturn short are related?
4. I know IEEE specifies minimum bearing insulation as 5 megaohms. However, I can’t see the shaft voltage jumping 2 megaohms of insulation. Also, a shaft grounding brush is in place. So, how did the shaft get magnetized & the bearing get the pitting marks?
5. Client is not interested in repairing the fault or demagnetizing the shaft. What implication would a magnetized shaft have on reliability?
Any answers or feedback would be most appreciated.
Regards,
Aditya
1. Rotor has an interturn short – impedance is reduced by 17 % compared to the factory values. Surge waveform shows separation when tested from either end (+ve & -ve). Cleaning did not help.
2. Generator shaft is magnetized, as are the centering rings of the endbells.
3. Bearing insulation resistance was 2 megaohms.
4. Exciter end bearing shows electrical pit marks, but not in the load zone.
5. About 20 grub screws used to lock the rotor wedges were missing. Located 14 so far, some stuck in the stator ventilating ducts. Many rotor wedges were thus loose.
6. Boroscope inspection under the retaining rings did not reveal any abnormality.
7. One rotor coil has shifted axially leading to partial blockage of some of the ventilating holes.
This is a 7 year old gas turbine generator which is started every day morning, run at full load & shut down at night (first time I’ve seen this).
Answers/opinion sought:
1. How often do you run generators with rotor interturn shorts? I have seen two earlier, but with minor impedance reduction (surge test would show separation of the waveforms).
2. At what percentage of impedance reduction would say that a repair is a must?
3. Is there any way in which the shaft magnetization & interturn short are related?
4. I know IEEE specifies minimum bearing insulation as 5 megaohms. However, I can’t see the shaft voltage jumping 2 megaohms of insulation. Also, a shaft grounding brush is in place. So, how did the shaft get magnetized & the bearing get the pitting marks?
5. Client is not interested in repairing the fault or demagnetizing the shaft. What implication would a magnetized shaft have on reliability?
Any answers or feedback would be most appreciated.