Given an air to water heat exchanger with the following characteristics:
Inlet temperature of Hot air: 750F
Outlet temperature of hot air: 400F
Flow: 10,000 SCFM
Pressure drop: 1" of Water
My question is: How to calculate the pumping power requirement for a fan that will help me to circulate the air through the heat exchanger?
I have found the folowing equation:
Power[HP] = Flow[CFM]*Pressure_Drop["W]/(6356*efficiency)
1- I'm not sure if this is the right equation that I should use. Could someone comment?
2- The flow in CFM at the inlet will be different than the one I will see in the outlet, because the density is different. So how should I calculate the required fan pumping power? Which value of CFM should I consider, inlet or outlet?
Inlet temperature of Hot air: 750F
Outlet temperature of hot air: 400F
Flow: 10,000 SCFM
Pressure drop: 1" of Water
My question is: How to calculate the pumping power requirement for a fan that will help me to circulate the air through the heat exchanger?
I have found the folowing equation:
Power[HP] = Flow[CFM]*Pressure_Drop["W]/(6356*efficiency)
1- I'm not sure if this is the right equation that I should use. Could someone comment?
2- The flow in CFM at the inlet will be different than the one I will see in the outlet, because the density is different. So how should I calculate the required fan pumping power? Which value of CFM should I consider, inlet or outlet?