Oct 2, 2013 #1 Clyde38 Electrical Joined Oct 31, 2003 Messages 533 Location US Is the fan load included in the reported nameplate efficiency (NEMA, IEC, IEEE, etc.)? I am referring to the fan attached to the shaft, not an external blower. Thanks . .
Is the fan load included in the reported nameplate efficiency (NEMA, IEC, IEEE, etc.)? I am referring to the fan attached to the shaft, not an external blower. Thanks . .
Oct 2, 2013 1 #2 electricpete Electrical Joined May 4, 2001 Messages 16,774 Location US Yes, motor is tested including any integral fan and associated losses will be part of windage losses. ===================================== (2B)+(2B)' ? Upvote 0 Downvote
Yes, motor is tested including any integral fan and associated losses will be part of windage losses. ===================================== (2B)+(2B)' ?
Oct 2, 2013 Thread starter #3 Clyde38 Electrical Joined Oct 31, 2003 Messages 533 Location US Thanks Pete, that is what I thought . . . Upvote 0 Downvote