Have a bit of a dilemma; contractor is proposing an anchor bolt to F1554 to Grade 55 - straightforward. However, when reviewing the mill cert, the tensile test result is 675 MPa. The specification, Table 3 gives a range of 517 to 655 (now why 517 and not 515? - conversion, I gather).
The dilemma is would one accept this material even though it has a tensile strength 20 MPa higher than the maximum given in the specification? We are in a tropical climate with temperatures seldom dropping below 24degC.
As a parallel query - why do they give a range rather than just a minimum strength? What is the significance of the range?
With![[cheers] [cheers] [cheers]](/data/assets/smilies/cheers.gif)
The dilemma is would one accept this material even though it has a tensile strength 20 MPa higher than the maximum given in the specification? We are in a tropical climate with temperatures seldom dropping below 24degC.
As a parallel query - why do they give a range rather than just a minimum strength? What is the significance of the range?