extended coverage start? 1

Status
Not open for further replies.

sprinkle2013

Computer
Joined
Aug 1, 2013
Messages
8
Location
US
What constitutes extended coverage? If I were using a residential 4.9 sprinkler in a corridor under NFPA 2007 13 11.2.3.3.6 specifies or when extended coverage sprinklers are used. Where does the extended start, 16'x16' , 20'x20'? What's standard 14'x14' spacing?
 
NFPA 13-2010 3.6.4.3 Extended Coverage Sprinkler: A type of spray sprinkler with maximum coverage areas as specified in sections 8.8 and 8.9 of this standard.
 
If you were using a residential 4.9 sprinkler, NFPA 2007 13 11.2.3.3.6 would be the wrong place to look for design criteria. You would want to check out 11.3.1 Residential sprinklers.

 

sprinkle2013 (Computer)


13 Aug 13 9:12





What constitutes extended coverage? If I were using a residential 4.9 sprinkler in a corridor under NFPA 2007 13 11.2.3.3.6 specifies or when extended coverage sprinklers are used. Where does the extended start, 16'x16' , 20'x20'? What's standard 14'x14' spacing?



maybe anything past 15 x 15


the designer picks the head they want to use. can be either a regular spray head or extended coverage. Either one can work on the same design. You just would use less heads with extended coverage.
 