PawSoxRule (Electrical) said:
... how do I know if they must be Explosion Proof etc? Is this something the customer must tell me? ...
The first thing you need is the customer's "Area Classification" drawing - occasionally called a "Control Drawing" There will be one - NEC 500.4.A. What ever the area is classified, the equipment must meet that spec.
If you get unlucky, the drawings will reference NEC 504, Zone 0, 1, 2. There still has to be a drawing - NEC 505.4.A. Although that only references industrial occupancies.
Uhhhhh .......... They don't have any drawings. Then that is your first task. There is a list of applicable standards in NEC 500.4. Most useful to me have been API RP 500, NFPA 30, NFPA 497. I have done little with Class II, so I can't help there. And API RP 505 for zones.
PawSoxRule (Electrical) said:
... I need to understand the difference between Explosion Proof, Intrinsically Safe, Class 1 Div 1, and Class 2 Div 2. ...
As mentioned, NEC Art 500.5, 500.6, Hazardous (Classified) Locations discusses Class I, Class II, Div 1, Div 2. Intrinsically safe, non-incentive, Purged and pressurized are described in 500.7. NFPA 496 discusses purged and pressurized. NEC 504 and NFPA 493 covers intrinsically safe.
PawSoxRule (Electrical) said:
... do I specify Explosion Proof valves just to be safe? ...
No - you figure it out, nobody wants to pay for or have to work on explosion proof gear unless they have to. As said earlier, if they don't have an Area Classification drawing, then you get to make one - if only just covering your area of work.
An un-asked aside: You are doing engineering for hire. Definitely get your Area Classification drawings stamped.
As already covered, the subject is complex, requires lots of judgment. Getting (hiring) experienced help is a good choice.