Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Excitation Transformer Sizing Calculation 1

Status
Not open for further replies.

Schwatzernov

Electrical
Sep 5, 2006
47
Hi,

I am power plant engineer, now I am designing 300MW coal fired power plant. The consultant request to submit calculation for sizing excitation transformer.

Can anyone advise me how to calculate excitation transformer size for static excitation system of turbo generator ?

Thank you,

Schwatzernov.
 
Replies continue below

Recommended for you

If you need a conservative ballpark figure use 4-5% of the set rating. This will cover you for most designs of turbo machines although I'm less certain about the big salient pole hydro machines. I suspect they may have greater requirements for the field excitation.

If you want an accurate answer then Edison has already given the best approach.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Hi.
What Edison saied.
excitation transformer it's part of static excitation system and static excitation it's part of generator.
For my pinion it's one package.
Regards.
Slava
 
Status