Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Evaporation Rate

Status
Not open for further replies.

visitor

New member
Mar 28, 2002
117
Will somebody help me how to calculate the approximate evaporation rate at a waterfall pond. The rate of recirculation water is @ 2,500 GPM.Ambient temperare is 85 deg. F during summer months ( wet bulb temp.),@80% relative humidity.



Appreciate any help.
 
Replies continue below

Recommended for you

There are a few variables not mentioned, so the best help I can offer is a text reference - See "Engineering Hydrology - Principles and Practices" by Victor Ponce. The publisher is Prentice-Hall (ISBN 0-13-277831-9).  Other texts on hydrology may have similar methods.
 
visitor, The basic equation I use for approximating Evap. rate is as follows:

E=(c*dT)/1000 Where:
E= evap. rate (gal/min)
c= system circ. rate (gal/min)
dT=system temp. diff. (deg. F)
(hot return temp. - cold supply)

Or you could use the general rule of thumb: E is approx. equal to 1% of recirc rate for every 10 deg. diff. between hot return and cold supply temp.

Hope this helps.

saxon
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor