nayusa

Mechanical
Mar 22, 2007
8
Dear All

I am planing to insulate the air duct serving a drying cabinet in my plant.

Surrounding temp = 22degC
Air temp at dehumidifier = 36degC
Air temp at drying cabinet = 28.5degC
Temp drop along the duct = 7.5degC

How could I do simple calculation to estimate heat transfer coefficient of the insulating material to be used?


sincerely
nayusa
 
Replies continue below

Recommended for you

You've gotten one part of the problem, which is the allowable temperature drop. The next things you need are a relatively accurate determination of the surface area of the duct, the airflow within the duct, and the type of airflow around the duct. The latter will determine the surface-to-air heat transfer coefficient. The airflow and temperature drop will determine the amount of actual heat energy loss incurred per unit time.

Then, the standard equation of Q = A*htc*deltaT is solved for the htc, and you can then look at various materials' properties and choose an appropriate one.

TTFN

FAQ731-376
 