I have a two story wood structure with wood floor/roof and wall plywood construction. I get very different seismic coefficient using the ASCE and UBC; which does not seem to be reasonable.
For ASCE equation V=(F Sds/R)W= 1.1*0.267/6.5 W = 0.045W
For UBC equation V=(Cv I/R T)W = (0.54*1.0/5.5*0.15) W = 0.65 W
For UBC equation Vmax=(2.5 Ca I/R)W = (2.5*0.36/5.5)W= 0.16 W; which I can divide by 1.4 to convert it to allowable stress design to get 0.12W.
My question is why the coefficient of 0.045W is so low with for ASCE design compared to 0.12W using the UBC? Is there any minimum limit for the seismic coefficient using the ASCM?
Thanks