I went to a house a contractor was building. The garage area had about 5 feet of backfill with gravel present. This is where he was going to pour his slab. The wall cracked while he was tamping it with his track hoe sitting in the middle of it (imagine that). The wall was constructed out of 12" masonry units. He reinforced it per the building code as he intrepreted it which was #4s @ 32". The corners were not reinforced. The placing per code for the steel is 8.75" from the soil side. That's where he put it, 8.75" from the soil side, 2.875" from the backfilled side (oops). Therefore it's significantly overstressed.
Additionally, the way I read the code, the reinforcing is based on equivalent fluid pressures based on active soil pressures (partially rigid floor system). Obviously, you don't want your garage slab to settle, therefore, it should be based on at rest pressure and rigidly restrained by the concrete slab. Per ASCE 7-02, for gravel, this should be an equivalent fluid pressure of 60 psf, which additionally blows out the footing. Again, per code, anything over 4 feet of backfill should have a "permanent" lateral restraint, otherwise, engineering design is required. To me, this means a concrete slab. Am I missing something?
Anyhow, here is the ethical delima:
When I stated all of this above, he said he was going to pursue another engineering buddy of his to come up and state that it was alright. I feel I have an obligation to let the building department know my findings on this wall in writing. Therefore, when something happens in the future, I'm covered. Is this wrong?
Additionally, the way I read the code, the reinforcing is based on equivalent fluid pressures based on active soil pressures (partially rigid floor system). Obviously, you don't want your garage slab to settle, therefore, it should be based on at rest pressure and rigidly restrained by the concrete slab. Per ASCE 7-02, for gravel, this should be an equivalent fluid pressure of 60 psf, which additionally blows out the footing. Again, per code, anything over 4 feet of backfill should have a "permanent" lateral restraint, otherwise, engineering design is required. To me, this means a concrete slab. Am I missing something?
Anyhow, here is the ethical delima:
When I stated all of this above, he said he was going to pursue another engineering buddy of his to come up and state that it was alright. I feel I have an obligation to let the building department know my findings on this wall in writing. Therefore, when something happens in the future, I'm covered. Is this wrong?