Emergency Shutdown Circuit Monitoring

Status
Not open for further replies.

markcraig

Electrical
Feb 2, 2007
6
Hi all,
I have an issue with design of an emergency shutdown circuit that can be monitored for open circuit and short circuit. Normally i would do this using UV trip coils but in this instance it is required that i use a NDE (normally De Energized) circuit as a failure of the shut down circuit must not stop the plant. Failure of the shutdown circuit is to bring up an alarm at the control panel.
Now i have seen a circuit used in this instance before where a small current is continually running through the system via some resistors and diodes. I just can't rememeber the configuration to save my life. I am thinking along the lines of a voltage divider. Am i even on the right path?
The shunt trip coils are 24V DC and i am not sure of the resistance at this time.

Any basic circuit would be greatly appreciated.

Thanks In Advance

Mark Craig
Electrical Engineer
Frontier Drilling
 
Replies continue below

Recommended for you

Look for 'trip circuit supervision' relays. They are used in most medium and large switchgear where the final tripping circuit is energise-to-trip. The principle is more or less as you describe. Have a look at Areva's MVAX series for a typical design.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Thanks for that it is what i was after. I have spent days looking up shut down monitoring and all sorts of things like that I never thought of trip circuit supervision.


Mark
 