jdbpe
Structural
- Aug 4, 2005
- 28
I have a 42 foot long W24 roof beam that needs to support 12 vertical feet of brick with stud backup below. I have C6 channel hangers every 6 feet supported from W24 and a plate in between 6 inch stud backup. The C6 hanger supports an 8x6 tube lintel with angle welded to it to catch brick. The centerline of backup is 17 inches away from the W24 beam. There will be a kicker from tube to W21 that is six feet away. Calculating the torsion along with dead and live load leads to a W24x84. Can I neglect the torsion if I provide a W10 beam on other side of W24 at every plate/C6 hanger location? The W10 beam will connect to the W21x44 six feet away. This location is at the metal deck roof level of a one story building