When analyzing elevated water tanks, AWWA D100-11 does not explicitly state that anchor bolts should be checked for combined tension and shear stresses.
I have always taken the statement from 3.3.2 Bolts - "bolts that are subject to shearing and tensile forces shall be so proportioned that the combined unit stress will not exceed the allowable unit stress for bolts in tension only" and interpreted it as:
T/An + V/An <= (4/3)*Flt for anchor rods, and checked the interaction accordingly.
I will admit that I only analyze 2-3 tanks a year, so I'm not the most well-versed, but I recently was discussing with a fellow professional who stated that they only check anchor rods for tension or shear separately as there is no explicit direction.
Anyone with more experience that can comment as to which approach is correct?
I have always taken the statement from 3.3.2 Bolts - "bolts that are subject to shearing and tensile forces shall be so proportioned that the combined unit stress will not exceed the allowable unit stress for bolts in tension only" and interpreted it as:
T/An + V/An <= (4/3)*Flt for anchor rods, and checked the interaction accordingly.
I will admit that I only analyze 2-3 tanks a year, so I'm not the most well-versed, but I recently was discussing with a fellow professional who stated that they only check anchor rods for tension or shear separately as there is no explicit direction.
Anyone with more experience that can comment as to which approach is correct?